Cracking 165F Barrier with B-2K
|
|
JimG |
Posted on 09/23/2014 8:14 AM
|
![]() 1 1/2 Pounder ![]() Posts: 834 Joined: October 23, 2008 |
When you short the input terminals for a thermocouple, the instrument will report ambient temperature. This should be the case for any Hottop K-type control board. How high is the indicated temperature when you close your NO switch? I might be concerned if it is above 150F. Jim |
|
|
IntrepidQ3 |
Posted on 09/25/2014 3:59 PM
|
![]() Newbie ![]() Posts: 46 Joined: December 15, 2013 |
The night I threw everything together (a few days ago) and gave it go, it would show 250F pressing the button when the drum was at 350F. I just gave it another go after reading your post (last night). This time the highest it read was 98F. Not sure what change since I put it together... I mean it has not moved one inch since I put the panels back on... Besides for this oddity, I would say project was a success. |
|