RobotDyn AC Light Dimmer Module
jake415
Right now I'm just testing the heater side since it seems simpler (no ZC). The PWM signal is connected and should work.
When I use CONFIG_PAC3 for phase angle control on heater, and test the robotdyn (Vcc to OT1, PSM to GPIO PIN 9), there are no flashing lights and the robotdyn seems completely inactive. When I use CONFIG_PWM for PWM on heater, same connections, there are flashing lights and the robotdyn works. I'd like to use phase angel control but so far no luck.
 
renatoa
PAC requires ZCD, that's why is not working
Without ZCD only PWM is available.
 
jake415
I didn't know that, problem solved ThumbsUp thanks
 
dpecsok
hello!
im using the RobotDyn module to control an 1200w AC vac motor using PAC2 mode. ive been testing with both the motor and a lamp as well. problem is that the motor or light is either OFF or at 50% and higher. below 50% it seems motor and light are bit jittery like its being pulsed on and off. any suggestions is very much appreciated!
dpecsok attached the following image:
screen_shot_2022-03-14_at_13135_pm.png
 
dpecsok
i read in a few other posts that this is common using PAC. i there a way to control the RobotDyn using PWM mode? if so what is the proper way to wire it? sorry im a noob ha!
 
renatoa
If motor is induction type, i.e. no brushes/sparks, then you need a special driver, called VFD, quite expensive.
PAC works for the so called "universal" motors, those that are noisy even without load, to distinguish them from induction motors, which are quiet.
Vac motors are universal type though, sounds strange what you report... connections from the diagram above are ok.

The bulb also should work ok, though... you should experience no flickering with PAC control. Please, can you post a short video clip to see the bulb behavior ?

PWM can be slow type, used to control heaters, in CONFIG_PWM mode, or fast type, output on IO3, to control DC fans or heaters using external drivers, choice depending on task.
 
dpecsok
thanks for your feedback, i will try to make a video soon..

Quote

renatoa wrote:
PWM can be slow type, used to control heaters, in CONFIG_PWM mode, or fast type, output on IO3, to control DC fans or heaters using external drivers, choice depending on task.


So in PWM mode its not possible to control an AC motor?
 
renatoa
The answer is no, for a mains powered AC motor.
As we can read the descriptions in the user.h section listing the various configs:


//#define CONFIG_PWM // slow PWM on OT1 (heater); fast PWM output (3.922kHz) on IO3 (DC fan); ZCD not required


... PWM on IO3 means using a MOSFET driver, for a DC motor.

For your task people usually use CONFIG_PAC2:

#define CONFIG_PAC2 // phase angle control using ICC on OT1 (heater) and OT2 (fan); IO2 used to read the ZCD


Note of the above: even if not specified, ICC is used on OT1, for heater only, not on OT2, where phase angle control is used for fan.

Even the other config modes listed after PAC2 can be used, depending on motor type and available electronics to drive it.

//#define CONFIG_PAC2_IO3HTR // phase angle control on OT1 (heater) and OT2 (fan); IO2 reads the req'd ZCD; IO3 reserved for fast PWM output for heater
//#define CONFIG_PAC3 // phase angle control on OT1 (heater) and OT2 (fan); IO3 reads the req'd ZCD; IO3 not available for output
//#define CONFIG_PAC2_IO3FAN // phase angle control on OT1 (heater) and PWM control of IO3 (fan); IO2 used to read the ZCD
 
renatoa
There is a possible reason that comes later in my mind...
A motor is an inductive load, compared to a heater, which is mainly resistive load, even if it looks as a coil Grin
A control element of an inductive load should be fitted with a RC circuit on the exit, called snubber.
The first version of this dimmer, from the very first post of this thread, lacks this circuit, being appropriate for resistive loads, or very low power motors.
There is a second version of this dimmer, signaled here first time in post #29 above, which is fitted with this snubber circuit, the components enclosed in ellipse in attached picture.
If you have the first version dimmer you have to attach these two components externally, on same output terminals as the motor, as you can see here:
https://en.wikipe...C_snubbers
The values of components, how well I am able to read on the image, seems to be 10nF/400V for capacitor, and 1kO for the resistor.
~~~
renatoa attached the following image:
top_3_1.jpg

Edited by renatoa on 03/14/2022 8:22 AM
 
dpecsok
renatoa thanks for your replies and input. heres a video, and you can see that there is a lot of flickering with the light and not so much dimming.
im thinking maybe the dimmer module is not working properly or im doing something wrong ha!
im looking into getting the updated version with the snubber circuits but im thinking that even without it shouldnt the light be dimming properly?

link to video:

Edited by renatoa on 03/16/2022 5:28 AM
 
renatoa
The only thing that comes in my mind at first look is that the zero cross pulses aren't triggered at the right moments.
It can be diagnosed, but requires some code changes.
How is the led on the board activity ? Follows the bulb ?
 
dpecsok

Quote

renatoa wrote:

The only thing that comes in my mind at first look is that the zero cross pulses aren't triggered at the right moments.
It can be diagnosed, but requires some code changes.
How is the led on the board activity ? Follows the bulb ?


So at 0% fan, no LED on. from 1-100% the OT2 LED on the TC4 & a LED on the Robotdyn turn on and stay on.
from 1-50%ish , the light im dimming just flickers a lot like the video i posted earlier. 50% and above its seems like the light gets a little brighter but not gradually, more like it steps up every 20% or so.

what code changes do you suggest to diagnose?
thanks!
 
renatoa
In my fork copy, in the interrupt routine serving ZC detection, added here:
https://github.co...l.cpp#L115

...some code that check if there isn't a parasite triggering of a false zero cross, after the very first, assumed the legit.

byte pinVal = digitalRead(INT_PIN);


   if (pinVal == HIGH) { 

      // false triggering filter
      if ((millis() - lastCross) < 4 ) {
         falseCross = millis() - lastCross;
         return;
      }

      // perform AC monitoring
      lastCross = millis(); // timer0
...


The falseCross variable, can be checked in the main application if you want more detailed diagnose.
It is forbidden to send some output on serial line inside a interrupt routine, that's why any relevant info you want to know have to be stored in variables and checked outside.
 
dpecsok
insert in between line 113 and 114?

...
void ISR_ZCD() {
TCNT1 = 0; // reset timer1 counter
byte pinVal = digitalRead(INT_PIN);
if (pinVal == HIGH) {

// false triggering filter
if ((millis() - lastCross) < 4 ) {
falseCross = millis() - lastCross;
return;
}

// perform AC monitoring
lastCross = millis(); // timer0
...


is this a fix or a way to check the timing? how do i see the results of the diagnosis?
 
renatoa
Stooop, please ! Grin
This code is for a different version of TC4, adapted for ESP family of processors, and posted only as a proof of concept.
Will not work by simply copy-pasted on original Arduino TC4, without a deeper understanding of programming.
For example, surely that first line time reset shouldn't be there... and also there should be a closing } bracket somewhere further in the code, else would not compile, etc...
Is better to wait for the current master of TC4 to add something equivalent for Arduino Uno, thoroughly checked, and committed in the official repository.

This code is both a fix for multiple parasite zero crossings, and also a diagnose method, by checking the falseCross variable.

Attached an image for a better understanding of the issue, which is VERY present in industrial environments, where a lot of heavy loads are started/stopped permanently.
But also in household scenarios, in my home the record was eight such parasite triggering, that forced me to fix them in code.
~~~
renatoa attached the following image:
image_2022-03-20_204259.png
 
renatoa
Before venturing too deep in these assumptions, a simple question: are you using OT2 for the fan control ? I.e. output pin D10?
Because, if reversed, in PAC2 mode the OT1 control is different than OT2 !
 
dpecsok
coding is not my specialty so im waiting till i know for sure from someone who knows better!

yes using PAC2 , OT2 for fan control
robotdyn VVC to OT2
GRD to IO2 GRD
ZC to IO2
PSM to D10

hopefully i have that correct
 
renatoa

Quote

robotdyn VVC to OT2


Vcc connection to OT2 is questionable, because you have no guarantee there is a firm voltage on that pin.
Also, there is no need for this connection, the RobotDyn board designer provided it for other custom applications. Not needed for TC4.
In all my usages of various board models of this design, at least four units that I remember atm, I don't connect the Vcc pin.
Edited by renatoa on 03/21/2022 8:05 AM
 
dpecsok
wow! i think you just solved my issues Grin pulled the VCC to OT2 and its working now with a light. now to try with a motor
 
renatoa
Credits goes to your Vcc <> VVC typo, that catch my attention Grin
 
dpecsok
fyi, i ordered the updated version with the snubber capacitors on the board but instead received an update to the updated version ha! looks like they removed the capacitors again .... size, heatsink, and AC connections are larger; about the size of an SSR now.

trying to add a picture as an attachment but its not working...
 
iPa
As soon I switched from ZCD module bought with the TC4 shield ("ZCDboard") to the ZCD from the Robodyn module ("ZCDrobodyn") I noticed a weird behavior change with the PID control. I made many tests to confirm this difference. For now I don't have any explanation, yes I should get out the oscilloscope...
Any ideas of explanation about this difference, welcome Grin

ZCDboard result:
A bit below the curve at the beginning but reached it soon, maybe need to increase ki
i84.servimg.com/u/f84/20/23/21/77/captur27.png

ZCDrobodyn result:
A lot more oscillations in this case
i84.servimg.com/u/f84/20/23/21/77/captur28.png
 
renatoa
Is the LED on Arduino board lit both cases ? i.e. zcd working, a/c detected.

Looks like you have on-off switching in the second scenario...
 
iPa
The oscilloscope revealed some interesting things:
- The signal polarity is not the same between this 2 boards !!
- If the board is to not connected to VCC the signal is less good drived (so better to connect vcc).

Need to have a look in the code to understand the impact of this reversed polarity, and what is expected.
Maybe @renatoa have you some information about that ?


ZCDboard with vcc
i84.servimg.com/u/f84/20/23/21/77/img_8013.jpg

ZCDboard without vcc
i84.servimg.com/u/f84/20/23/21/77/img_8012.jpg

ZCDrobodyn note the inverted polarity compared to the ZCDboard (with vcc)
i84.servimg.com/u/f84/20/23/21/77/img_8010.jpg

ZCDrobodyn without vcc
i84.servimg.com/u/f84/20/23/21/77/img_8011.jpg

if someone has schematics about this 2 boards I am interested
edit1: I found schematic for the Robotdyn but not for the NZDboard (mine is a verson 6.2)

edit2: Found in the code:
Expected> logic low indicates zero cross
Interrup on falling edge> attachInterrupt( EXT_INT, ISR_ZCD, FALLING );
That means, ZCD interrupt will occurs about 1mS later with ZCDRobotdyn (1/2 period = 10mS = 10%), is that enough to explain the difference behavior, probably. Asap I will test with interrupt on the rising edge with the ZCDRobotdyn.
Edited by iPa on 03/27/2022 10:44 PM
 
renatoa
Could be related to similar processes, as investigated some posts above, starting with #51.

If not intriguing enough, in my TC4ESP fork I changed also the polarity, but for other reasons, without scoping the ZCD signal... Grin

My posts about with/without Vcc pin connected are related to robotdyn board only, never used another make, so can't comment about their behavior, without schematic.